Assistance requested to clerify transformer calculations (open delta) and square mils versus circular mils.
I am reviewing some books of transformer calculations and formula's. In my review, I have discovered that the author may have made a mistake. I would like some assistance in reassuring myself that I may be correct in my assumptions.
********************************************** 1st topic, transformer calculations----
Two question are listed within this book in regard to open delta kva ratings.
1st question-------If you were operating three 25kva 1ph transformers in a delta connected 3ph system and removed one transformer, what is the kva capacity of the two remaing transformers connected delta three-phase?
The answer given in the book indicates 75kva x .577 = 43.275kva.
2nd question-------Three 10kva transformers are delta connected, if one phase opens up, what will be the kva rating of the open delta?
The answer given in the same book indicates 10kva x .577 = 5.77kva.
Open winding or removed winding, would not the electrical impact of the kva remain the same.
Do you agree that the answer to question 2 above should really by 30kva x .577 = 17.3kva.--or is there something I'am not grasping here?
***********************************************
Square mils vs circular mils-----
Book indicates the following:
1 circular mil = .7854 square mils
1 square mil = 1.2732 circular mils
circular mils = square mils x 1.2732
square mils = circular mils x .7854
It seems to me that, if one circular mil = .7854 square mils then circular mil would = square mils x .7854 not 1.2732.
Am I correct in assuming the author may have made an error?
Confused?
***********************************************
[ August 04, 2003, 02:32 PM: Message edited by: champion ]
I am reviewing some books of transformer calculations and formula's. In my review, I have discovered that the author may have made a mistake. I would like some assistance in reassuring myself that I may be correct in my assumptions.
********************************************** 1st topic, transformer calculations----
Two question are listed within this book in regard to open delta kva ratings.
1st question-------If you were operating three 25kva 1ph transformers in a delta connected 3ph system and removed one transformer, what is the kva capacity of the two remaing transformers connected delta three-phase?
The answer given in the book indicates 75kva x .577 = 43.275kva.
2nd question-------Three 10kva transformers are delta connected, if one phase opens up, what will be the kva rating of the open delta?
The answer given in the same book indicates 10kva x .577 = 5.77kva.
Open winding or removed winding, would not the electrical impact of the kva remain the same.
Do you agree that the answer to question 2 above should really by 30kva x .577 = 17.3kva.--or is there something I'am not grasping here?
***********************************************
Square mils vs circular mils-----
Book indicates the following:
1 circular mil = .7854 square mils
1 square mil = 1.2732 circular mils
circular mils = square mils x 1.2732
square mils = circular mils x .7854
It seems to me that, if one circular mil = .7854 square mils then circular mil would = square mils x .7854 not 1.2732.
Am I correct in assuming the author may have made an error?
Confused?
***********************************************
[ August 04, 2003, 02:32 PM: Message edited by: champion ]