DLaHaye
Member
- Location
- Grapevine ,Texas USA
I have current two situation at some our facilities on a existing transformer installation . I am trying to correct the issues with limited cost and impact to system.
Scenario #1 : 15 KVA Single Phase 480 Primary /240-120 Secondary
All equipment is mounted outside , transformer is less than 10ft. from panel
Primary has a 40 amp OCPD with #8 wire
Secondary - is supplying a 200 amp main breaker in panel on 3/0 wire
Question: I know the secondary panel is over sized for the capacity of transformer but the secondary conductors are protected. The way I understand it I am not required to have Secondary OCP for the transformer given it is outside and less than 10ft. from panel as well as Primary OCPD is sized @125%. According to 240.21(C) (2)&(4) also , Table 450.3(B). Would that be correct and can I leave installation alone?
Scenario #2 : 25 KVA Single Phase 480 Primary /240-120 Secondary
All equipment is mounted outside
Primary has a 70 amp OCPD with #4 wire
Secondary - is supplying a 200 amp main breaker in panel on #2 wire (which I know is not correct)
Question : My thoughts to correct this would be to change the 200 amp MB to 110 amp to protect my secondary conductors. Would this be a proper solution? ( other than pulling 3/0 wire)
Scenario #1 : 15 KVA Single Phase 480 Primary /240-120 Secondary
All equipment is mounted outside , transformer is less than 10ft. from panel
Primary has a 40 amp OCPD with #8 wire
Secondary - is supplying a 200 amp main breaker in panel on 3/0 wire
Question: I know the secondary panel is over sized for the capacity of transformer but the secondary conductors are protected. The way I understand it I am not required to have Secondary OCP for the transformer given it is outside and less than 10ft. from panel as well as Primary OCPD is sized @125%. According to 240.21(C) (2)&(4) also , Table 450.3(B). Would that be correct and can I leave installation alone?
Scenario #2 : 25 KVA Single Phase 480 Primary /240-120 Secondary
All equipment is mounted outside
Primary has a 70 amp OCPD with #4 wire
Secondary - is supplying a 200 amp main breaker in panel on #2 wire (which I know is not correct)
Question : My thoughts to correct this would be to change the 200 amp MB to 110 amp to protect my secondary conductors. Would this be a proper solution? ( other than pulling 3/0 wire)