I am wiring up a 225KVA transformer to test 480V/460/440 equipment around the shop. We have a 208 service coming into the building and the transformer is 440v Prim 208 Sec. I will be wiring it in reverse in order to get the 440v need to test equipment. I am only going to be connecting one 100 amp disconnect So I need to make sure my calculatins are correct. Money is also an issue of course so I am going to try to make this cost effective too.
I am not sure if I should leave the transformer wired at a specific voltage since many of the machines I will be testing will have control transfromers in them and they may be wired at a specific voltage in order to ensure proper operation of the coils on the contactors. I am thinking of wiring it for 460v since that is middle of the road and should cover me.
There is a spare 200 amp breaker in the panel if I where to use this I would be able to get 86 amps on the secondary wired at 480v correct? if the xfrm was wired for 440 I would have 94 amps. 90amps @ 460v
If I have #4/0 75c wire coming from the 200 amp breaker in the main panel feed a fused 200amp disconnect then feed the xfmr prim with #4/0 then have #2 wire off the sec feed a 90 amp fused disconnect I should be ok?
I am not sure if I should leave the transformer wired at a specific voltage since many of the machines I will be testing will have control transfromers in them and they may be wired at a specific voltage in order to ensure proper operation of the coils on the contactors. I am thinking of wiring it for 460v since that is middle of the road and should cover me.
There is a spare 200 amp breaker in the panel if I where to use this I would be able to get 86 amps on the secondary wired at 480v correct? if the xfrm was wired for 440 I would have 94 amps. 90amps @ 460v
If I have #4/0 75c wire coming from the 200 amp breaker in the main panel feed a fused 200amp disconnect then feed the xfmr prim with #4/0 then have #2 wire off the sec feed a 90 amp fused disconnect I should be ok?