Hello All
First time poster. Hoping to get some supporting information on a project I am looking at.
Here goes
Deer Park , NY
Existing on Job
45kva step down transformer. 277/480v #2 wire Protected with 100 breaker. Which is approx 250 feet away from main service
Feeding 120/208 100 amp main breaker panel
The landlord is requiring 150 amps 120/208 volts
I am on the fence
I want to install a 75kva transformer and install a 150 amp 120/208 main breaker panel on existing feed
#2 wire 75c @ 480 volts up to 300 plus feet will support the 75kva transformer @ 90 amps Wire rated up to 115 amps
Do I need to run a new feeder for transformer
Thank you for any feed back