480p 3 phase
220s 3 phase
112.5 Delta/Delta transformer (required because 75kva too small)
Secondary load 80 kva (stand alone machine tool)
Do I have to size the system to the transformer?
or
Can I size the system to the load?
If sized by the size of the trans: 175a p breaker, #2/0 p conductors
400a disconnect,
#750 kcmil s conductors
If sized to the load:
125a p breaker, #2 p conductors
400amp disconnect (with 300amp fuses)
#4/0 s conductors
Why is this (or not) ok?
Thanks
220s 3 phase
112.5 Delta/Delta transformer (required because 75kva too small)
Secondary load 80 kva (stand alone machine tool)
Do I have to size the system to the transformer?
or
Can I size the system to the load?
If sized by the size of the trans: 175a p breaker, #2/0 p conductors
400a disconnect,
#750 kcmil s conductors
If sized to the load:
125a p breaker, #2 p conductors
400amp disconnect (with 300amp fuses)
#4/0 s conductors
Why is this (or not) ok?