Transformer Clearance

Status
Not open for further replies.

trallio

Member
I have two outdoor oil filled transformers. Both have 13.8KV primaries.
One has a 4160V secondary, the other has a 480V secondary. They are 750KVA & 2500KVA.

Is there a minimum spacing requirement between these transformers?

Is there a requirement for a fire wall or similar?
 
They aren't necessarily POCO transformers. If that is the case, the NEC would apply. As far as spacing goes, I think you have to follow the manufacturer's instructions.

I doubt you need a fire wall, but I do remember seeing something that if it is oil filled, you need to consider the possible effects of flammable oil blocking an exit - or something like that.

If the transformer is away from the building, probably not a problem.

Steve
 