transformer clearance

Status
Not open for further replies.

bsh

Senior Member
Per NEC 110..26 (A) working space per table 110.26 (A)(1) is requied for equipment "likely to require examination, adjustment, servicing, or maintenance while energized". For dry type transformers I'm of the opinion that the required working space per table 110.26 (A) (1) probably doesn't apply. I'm looking for agreement, disagreement other thoughts?
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Retired Electrical Engineer
I agree. When I design the layout of an electrical room, I leave room to work around the transformers, but I do not make a special effort to ensure the spacing of 110.26 is available.
 