vw55
- California
I understand the two methods of transformer protection as outlined in Article 450, but I have concerns when the transformer conductors are oversized to allow Method 2 where the secondary is to be protected by a panel's main circuit breaker. For instance, if a transformer has a primary rated current of 75A, and a secondary rated current of 150A, the contractor installs a 150A breaker in a distribution panel protecting the primary feeder per Article 240, runs #1/0 primary conductors to the transformer, no secondary overcurrent protection at the transformer, and then runs #3/0 secondary conductors that terminate in a 200A panel with a 200A main circuit breaker, this installation will be compliant with both articles 450 and 240. Although the conductors are protected, is the transformer truly protected?
What happens to the transformer windings, if for whatever reason, the transformer draws 99A on the primary for an infinite amount of time? Neither breaker would trip because primary breaker rating is not exceeded, but the transformer primary is subjected to 99A while only rated at 75A. Would the secondary be self-limiting and only allow 150A to flow during this time or would 198A actually flow?
I understand they are probably over-engineered and will withstand such conditions, but for how long?