X xformer Senior Member Location Dallas, Tx Occupation Master Electrician Oct 18, 2012 #1 Are Transformer primary conductors sized according to 215.2?
david luchini Moderator Staff member Location Connecticut Occupation Engineer Oct 18, 2012 #2 Yes. Of course 215.2 only specifies a minimum ampacity, they could be larger. And they must be properly protected per 240.4.
Yes. Of course 215.2 only specifies a minimum ampacity, they could be larger. And they must be properly protected per 240.4.