Hey guys,
My boss gave me a 30kva transformer, delta to wye, 3 phase, 480v to 120/208v. It’s feeding a breaker panel with a 60A main. My boss says to feed the transformer with 10awg conductors on the primary protected by 30A fuses. On the secondary to feed the panel with 6awg conductors with a 60A main breaker in the panel. Is this correct?
How and when do I choose to downsize the primary in conjunction with the secondary?
My thoughts are to feed the primary with 8awg and protected by 50A fuses. And feed the 60A main breaker with 4awg conductors.
My boss gave me a 30kva transformer, delta to wye, 3 phase, 480v to 120/208v. It’s feeding a breaker panel with a 60A main. My boss says to feed the transformer with 10awg conductors on the primary protected by 30A fuses. On the secondary to feed the panel with 6awg conductors with a 60A main breaker in the panel. Is this correct?