Transformer Current Loss With Little Voltage Loss

Status
Not open for further replies.

bhsrnd

Senior Member
Location
Fort Worth, TX
Is it ever possible that amperage levels provided by the utility could sag without sagging the voltage to below nominal levels (i.e.- 480v)? If so, would this be transformer related?
 
I don't follow. If the utility amps "sag," that is get lower, that will increase (not decrease) the voltage at every point along the line. What are you trying to ask?
 
If I understand the question right, the answer is basically no. Ohms law must hold at any point in the system. Say your load is a 480 ohm resistor. At 480V, it normally draws 1 Amp. If the utility can only supply 1/2 amp (say, because it is overloaded) then the voltage across the load will have to drop to 240V. There is no way the current can be anything other than 1 amp if the voltage is 480V and the load is 1 ohm.

Motor loads and capacitive loads and nonlinear sources and loads make the issue a little more complicated. And if we consider standing waves, then the voltage and current can be different at different points along a transmission line. But I think it would be a very rare case if you measured normal voltage but the utility couldn't provide the current draw.

Edit: I am also assuming you are measuring the voltage with the load connected. If you measure the voltage without the load connected, the answer would be a definate yes.
Steve
 
Last edited: