I was wondering if anyone could show me the calculation for figuring out the max current on the line side of a transformer we have here at our plant. The transformer is a 25MVA, 230KV to 4.16KV Delta-Wye transformer. From what I read, the load side can produce up to 3500Amps, but I was wondering what amp load the transfer will draw on the line side.

Thanks for the help

Mull982
 
Couple of basic formulas:

P = sqr(3)EI
And that is truth for both sides of the xmf (for 3 phase).
P(pri) = P(sec)

For the primary side,
I = P/E/(sqr(3)) = 25x10^6/230x10^3/1.732

For the secondary side,
I = P/E/(sqr(3)) = 25x10^6/4.16x10^3/1.732

Turns ratio of the xfm = voltage ratio = 1/current ratio:
E(pri)/E(sec) = I(sec)/I(pri)

carl

(hit the post button too soon)
 
Last edited:
mull982 said:
Hello

I was wondering if anyone could show me the calculation for figuring out the max current on the line side of a transformer we have here at our plant. The transformer is a 25MVA, 230KV to 4.16KV Delta-Wye transformer. From what I read, the load side can produce up to 3500Amps, but I was wondering what amp load the transfer will draw on the line side.

Thanks for the help

Mull982

Give or take 63A @ nominal 230kV.