Transformer damage curve

Status
Not open for further replies.

binwork91

Senior Member
Location
new york
Occupation
electrical engineer
Does code require to protect the transformer damage curve?

Can primary side breaker or fuse curve on the right side of the transformer damage curve?
 

mayanees

Senior Member
Location
Westminster, MD
Occupation
Electrical Engineer and Master Electrician
Do you know the reason why we don't need to protect transformer from damage?
I think we need to protect the equipment and conductor.
Ideally your primary device slices to the right and your secondary device shades to the left of the ANSI curve to provide complete protection, but the code requirement is 450.3(A) and (B). And setting of devices is always limited by the upstream allowance and by the devices in the primary and secondary.

Conductor protection is required as well per the 310 tables.
 

binwork91

Senior Member
Location
new york
Occupation
electrical engineer
You should protect the transformer, however that is not an NEC requirement. The NEC is about protecting conductors not equipment, see 90.1.
Do you mean we don't need to care about damage curve base on NEC code?
Is there any code require to fully protect the transformer, and make primary side OCDP curve on the left side transformer damage curve?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Do you mean we don't need to care about damage curve base on NEC code?
Is there any code require to fully protect the transformer, and make primary side OCDP curve on the left side transformer damage curve?
The NEC has requirements for transformer protection based solely on 125% of the full load (either on the primary or the secondary), no other transformer characteristic is mentioned or considered.
 

paulengr

Senior Member
Why are you worried? Transformers can be overloaded by a lot with little to no harm done. Industrial plants rarely do this but utilities routinely do.

Whoever asked about primary/secondary there are a couple advanced tricks I’ve done. One is with a relay/breaker on the primary side you can use a looser curve when closing the breaker in to avoid the magnetizing curve then switch to a tighter setting once it calms down (current under name plate). Another option is a virtual breaker since the secondary side current is high and it’s hard to eliminate the zone between the secondary breaker and the transformer secondary. Place bushing CTs on the secondary lugs and feed these to a protection relay to trip the primary side. Then you can trip as low as you want with primary side protection “only” although technically you have both.
 

xptpcrewx

Power System Engineer
Location
Las Vegas, Nevada, USA
Occupation
Licensed Electrical Engineer, Licensed Electrical Contractor, Certified Master Electrician
Does code require to protect the transformer damage curve?
The answer is yes. Refer to NEC section 110.10 (Circuit Impedance, Short-Circuit Current Ratings, and Other Characteristics).

Can primary side breaker or fuse curve on the right side of the transformer damage curve?

If the TCC is on the right side of the damage curve, the transformer will not be protected. There two parts to a transformer damage curve - thermal and mechanical. The ratings/settings in Article 450 are maximum ratings/settings and may not adequately protect equipment since they do not account for thermal and mechanical damage characteristics. You can refer to the IEEE Buff Book for some guidance on transformer protection.
 