Do you know the reason why we don't need to protect transformer from damage?No, you only need to protect within the parameters of tables 450.3 (A) & (B)
Ideally your primary device slices to the right and your secondary device shades to the left of the ANSI curve to provide complete protection, but the code requirement is 450.3(A) and (B). And setting of devices is always limited by the upstream allowance and by the devices in the primary and secondary.Do you know the reason why we don't need to protect transformer from damage?
I think we need to protect the equipment and conductor.
You should protect the transformer, however that is not an NEC requirement. The NEC is about protecting conductors not equipment, see 90.1.Do you know the reason why we don't need to protect transformer from damage?
I think we need to protect the equipment and conductor.
Do you mean we don't need to care about damage curve base on NEC code?You should protect the transformer, however that is not an NEC requirement. The NEC is about protecting conductors not equipment, see 90.1.
The NEC has requirements for transformer protection based solely on 125% of the full load (either on the primary or the secondary), no other transformer characteristic is mentioned or considered.Do you mean we don't need to care about damage curve base on NEC code?
Is there any code require to fully protect the transformer, and make primary side OCDP curve on the left side transformer damage curve?
Thank you.The NEC has requirements for transformer protection based solely on 125% of the full load (either on the primary or the secondary), no other transformer characteristic is mentioned or considered.
The answer is yes. Refer to NEC section 110.10 (Circuit Impedance, Short-Circuit Current Ratings, and Other Characteristics).Does code require to protect the transformer damage curve?
Can primary side breaker or fuse curve on the right side of the transformer damage curve?