I was wondering if someone could confirm it's okay to mount the disconnect switch for the transformer inside the electrical room as long as the transformer is field marked with its location according to 450.14? See drawing attached. Thanks ahead of time!
Sent from my SM-S918U using Tapatalk
Thank you for providing the sketch, it sure helps us understand a lot.
It would also help to see the corresponding single line sketch, that shows electrically how everything in the scope of this question, interacts with each other.
To answer the question about the location constraints on this disconnect, it would also depend on the following:
A. Is it an interconnection on the supply side [705.12(A) in NEC2023, formerly 705.11] of the service disconnect, or the load side [705.12(B) in NEC2023]?
B. Is the disconnect in question on the building side, or inverter side of the transformer?
There are situations which would have length constraints in this application:
1. A disconnect for a supply side interconnection (now considered a service disconnect in NEC 2023). Its line-side conductors may be limited in length, with specifics that depend on your NEC edition. The most restrictive has been 10 ft, and more recent editions have given more flexibility to this in commercial applications.
2. A disconnect on the inverter side of the transformer (i.e. the secondary) is governed by one of the options in 240.21(C). Inside a building, there are length constraints, and context rules to each length constraint.