So if you disconnect the transformer primary everything is disconnected. Why do you need a main connection with this rule?The primary disconnect is the only "disconenct" required by Art 450 as "disconnecting" the primary obviously disconnects the secondary. As david points out, it's the rules associated with Art 240 and 408 that address secondary disconnecting which is most often related to the device served and overcurrent.
Sorry, don't understand your question.Why do you need a main connection with this rule?
See post #2You now need a main disconnect for any transformer. This disconnect is located before the primary side of a transformer. If you disconnect the primary of a transformer everything is disconnected. If everything gets disconnected why do you need a main disconnect after the seperately derived system?
WHAT'S the question?Thank you but that wasnt the question
Go back and read post 2 again. No main disconnect is required on the secondary side of the transformer. In almost all cases you need overcurrent protection for the secondary conductors and in some cases you need overcurrent protection for the transformer. The installation of the required overcurrent protection almost always results in some type of disconnecting means.You now need a main disconnect for any transformer. This disconnect is located before the primary side of a transformer. If you disconnect the primary of a transformer everything is disconnected. If everything gets disconnected why do you need a main disconnect after the seperately derived system?
IMHO if the transformer is providing power to a panelboard, the panelboard is required to have an OCPD but the secondary of the transformer is not.Since the code now requires a transformer disconnect for all transformer. On the primary side why do you need a main disconnect after the secondary? Wont the new rule accomplish the same job?
There's not enough information given to determine if the secondary of the transformer is required to have an OCPD.IMHO if the transformer is providing power to a panelboard, the panelboard is required to have an OCPD but the secondary of the transformer is not.