Transformer Disconnect
PEL11
I'm coming out of the MDP and running about 100 feet to a new electrical room, and in the room I'm setting a new transformer. My drawings show a disconnect on the primary side of the transformer, do I really need one?
Local ammendments may require the xfmr disconnect though. I've run into that requirement but can't remember which state it was.
How about if I came out of the MDP, when 10 feet to a transformer, left the transformer and went 100 feet to a new electrical room. Would the code require a disconnect on the secondary side?
Probably.
For 600V or less primaries the NEC never requires a secondary disconnect. However, if the primary OCPD can only be greater than 125% of FLA if a secondary OCPD has been provided. Also, the secondary conductors neede to be protected ( there are several ways in article 240) so that usually means a secondary disconnect will be used. And finally 408 requires that a lighting and branch circuit panelboard have a main device some place.
engy said:
City of Chicago is one.
Engy
Can you site the Chicago Code Section that requires the primary disconnect? I've heard that it is a requirement, but have not been able to locate it.
Thanks,
Brian
Many factors come in to play on this one.
Possible tap rule consideration ? Is the feeder on the secondary side ran outside of the building ? What type of load is on the secondary side. Electrical room ? Remote building or structure?
Without more info I could not give a definte answer that is backed up with NEC requirements , not to mention additional state,city,county,etc. codes.
My opinion based on the info stated would be maybe.:D
ibew441dc
:cool: new question related; coming from a 10' gutter, does a 400 amp service, when the service entrance conductors do not exceed 15' in length, terminate to a main breaker, have to be fused? there is a total of 7 services that enter that building. Only three are in use. The building caught fire not too long ago
My original question, or at least what it should of been last night was, does it have to be a fused disconnect? Since the S.E.C. do not exceed 15' in lenght, can't it be a non-fusable disconnect?