B brother Senior Member Location "I have learned, in whatsoever STATE I am, therewi May 27, 2006 #1 where can i find where on the LOAD side of the transformer there is suppose to be a disconnected within 25ft of the transformer for that load?? Or something that talks about the 25ft. thanks.
where can i find where on the LOAD side of the transformer there is suppose to be a disconnected within 25ft of the transformer for that load?? Or something that talks about the 25ft. thanks.
J jtester Senior Member Location Las Cruces N.M. May 27, 2006 #2 There is no requirement for a transformer disconnect, but in many cases there is a requirement for secondary conductor protection. Look at 240.21(C). Jim T
There is no requirement for a transformer disconnect, but in many cases there is a requirement for secondary conductor protection. Look at 240.21(C). Jim T