vg-kmb
Member
- Location
- New Jersey
Installed a fused 300A, 480/277 volt, 3 phase feeder from a 400 amp switch. The feeder is 350s run in 3" conduit approx. 250'. The feeder terminates in a 400A, 600V, non-fused disconnect, the directly to a 225 kVa, 480/120/208 volt step down transformer. From the transformer, a 4" conduit with 500s and a 3" conduit with 3/0s are run into a 12"x12"x6' trough. Tapped from the trough are (2) 200A, MCB panels and (2) 100A, MCB panels. The inspector failed this installation stating it is a double tap at the transformer secondary and to either install a 600A, 120/208 3 phase disconnect after the transformer (no room) or feed all panels with 500s. Any input on this inspectors interpretation would be appreciated.