Transformer feed

Status
Not open for further replies.
It's going to depend on how you choose to protect the transformer and the OCPD rating on the primary. Rated primary current is 25,000VA ÷ 480V = 52A. See Table 450.3(B). 125% is 65A. The protection schema available to choose from are Primary Only, and Primary And Secondary. Quite often inadvertent secondary protection presents itself in the form of load-side panel protection... but this does not mean you have to use the P&S schema.
 
According to NEC Table 450.3(B), Art.215.2.1(a) and 240.4,
in my opinion, 125% of rated current will be 65 A primary and 136 A secondary. A 70 A breaker for primary and 150 A for secondary and as per Table 310.15(B)(16) 4awg primary and 1/0 secondary as a minimum cross section area for copper conductor 75oC insulation.
You have to check the voltage drop-no more than 5% total [3% per feeder.] Art.215.2.1(b)
Informational Note No. 2.
 