Are there any code or UL issues with feeding a transformer with a Thermal-Magnetic molded case breaker and a contactor to control the energazation of the feeder circuit? We have a customer that wished to have remote control open/close to energize the transformer feeder circuit and are trying to avoid using a more expensive Power Circuit Breaker with open/close capability.
I don't believe there are any issues as long at a T-M breaker is used (not instantaneous magnetic only) but wanted to be sure I wasn't missing anything.
I don't believe there are any issues as long at a T-M breaker is used (not instantaneous magnetic only) but wanted to be sure I wasn't missing anything.