Transformer feeder controlled by contactor

Status
Not open for further replies.

mull982

Senior Member
Are there any code or UL issues with feeding a transformer with a Thermal-Magnetic molded case breaker and a contactor to control the energazation of the feeder circuit? We have a customer that wished to have remote control open/close to energize the transformer feeder circuit and are trying to avoid using a more expensive Power Circuit Breaker with open/close capability.

I don't believe there are any issues as long at a T-M breaker is used (not instantaneous magnetic only) but wanted to be sure I wasn't missing anything.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
No issues in doing that, except that if it is going to be energized for long periods of time, i.e. weeks / months at a time, I would use a mechanically latched contactor and separate Open / Close commands. Just be careful in selecting the contactor, it needs to have a relevant INDUCTIVE load rating, which will be lower than the RESISTIVE load rating.
 