wallypiper
 - Atlanta, GA, USA
This has been discussed here in a variety of ways but I'd like some clarification/confirmation on a particular situation.
A european machine manufacturer commonly provides a transformer with their machine which runs on 400/3. They provide all secondary wiring and overcurrent protection (at the machine, based on tap rules) and even the wire trough for the secondary wiring.
The transformers are typically significantly oversized for the secondary load. They admit this and offer no technical explanation. It is easy to see when looking at their data. Presumably it has to do with availability, stocking decisions etc.
As part of our role in projects involving this equipment we have to list all of the electrical loads being installed. It's easy enough to get the KVA of the transformer and list the load based on that and the primary voltage (nearly always 480/3), but that results in oversized primary feeders based on the secondary load that will be served.
The rules for primary overcurrent protection seem to specify only the MAXIMUM allowed. As is often the case in the NEC, exact reading of the words is important. Can the primary feeder be sized based on the secondary load as long as the overcurrent protection for that feeder is also sized that way? The difference can be significant. I've seen it as much as 200 KVA. The transformer is not general purpose. It is dedicated to this one machine although it is installed separately. That is, it is not physically part of the machine but is installed next to it.
You don't have to buy the transformer from them, but if you provide it yourself you have to get a move on because availability of 480-400 transformers is not good in the US so they are frequently ordered from the machine supplier to avoid issues with delivery. If you bought it here, you would definitely try to get something closer in size to the actual secondary load. For what it's worth, we're talking about 400 to as much as 1200 KVA.