I have an existing transformer servicing an industrial building. The service conductors run underground from the transformer to the main switchgear outside.
I want to tap a new feeder from that transformer to service an addition to the building. Can I run the feeder taps along the exterior wall instead of underground trenching? I could not find any restriction in NEC regarding running taps on lengths >25ft, except for mentioning that feeders have to be "protected against physical damage". Is that open to AHJ interpretation, or if I use a RMC conduit / RGC conduit that should be sufficient protection?
I want to tap a new feeder from that transformer to service an addition to the building. Can I run the feeder taps along the exterior wall instead of underground trenching? I could not find any restriction in NEC regarding running taps on lengths >25ft, except for mentioning that feeders have to be "protected against physical damage". Is that open to AHJ interpretation, or if I use a RMC conduit / RGC conduit that should be sufficient protection?