I saw an interesting transformer panel installation I can't quite get my mind around.
480 primary 100 amp feed to 75 KVA transformer 480x120/208
secondary to a 200 amp main 42 space 120/208 panel, bottom fed.
At the panel top lugs, 4/0 copper to an adjacent 30 space 120/208 panel.
Seems like there should be a main for the second panel, as its not protected where it receives its supply.