Transformer for a single piece of equipment

Status
Not open for further replies.

Richterfan

Member
Location
Danbury,Ct
I have to install a 208v 3 ph 75kva xformer to a 480v 3 ph piece of equipment. Do I need to run a conductor from the xformer to building steel, or since its supplying a single piece of equipment I dont need to go to building steel and can use just bonding bushings?
 
This is a step-up transformer? Will the secondary be operating as ungrounded?
It doesn't matter. The answer is the same for both grounded and ungrounded systems. A connection to a grounding electrode is required. The only difference is that the grounded system will have a system bonding jumper and the ungrounded one won't.
 
Its a step up, and its straight 208 in and straight 480 out. The conductors feeding the xformer had a ground in it to the disconnect, so if I carry it through I dont need to go to building steel or I do?
 
Its a step up, and its straight 208 in and straight 480 out. The conductors feeding the xformer had a ground in it to the disconnect, so if I carry it through I dont need to go to building steel or I do?

you need to connect to a GE. you also have to bring in the EGC with the feed conductors. They are seperate.

i realize this sounds absurd (and probably actually is absurd) but it is what is required to comply with code.
 
It doesn't matter. The answer is the same for both grounded and ungrounded systems. A connection to a grounding electrode is required. The only difference is that the grounded system will have a system bonding jumper and the ungrounded one won't.

Got a code reference? And if ungrounded a connection to what?
 
Rob,
250.30. (A) is for grounded system and (B) is for ungrounded systems. The only real difference is that you don't have a system bonding jumper or a grounded conductor with an ungrounded system.
 