Transformer for cooling tower.

Status
Not open for further replies.

darekelec

Senior Member
Location
nyc
A friend asked me to help him with a question.
What transformer and ocpd to use for a cooling tower that has technical info :
FLA 137A
MCA 142A
Max ocpd 150A
460V 3ø 60 Hz
Is it 112.5 or 150 kVA Y/D (corner grounded) transformer and 350 A ocpd on primary or 400?
I would go with 150 kVA

Is it common to size choose a transformer and load it 100%

Thank you in advance
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
What motors (HP) are involved ? any drives ??

112.5 appears undersized.
What is your primary voltage.
 
Looks like you're stepping up from 208 to 480, yes?
Is the transformer rated for step-up? Does it have a neutral point on the high side?
Corner grounding always raises my suspicion on things like this (like "why don't they have a neutral?). It also makes it harder to install some VFDs.

I'd go with the 150kva, too. Probably have a longer life and leaves room for expansion.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
Without knowing the nature of the load I would not speculate on the size. I would not even consider anything other than a 208 delta primary with a 480 Y secondary to avoid a lot of other issues. Also this set up will need both primary and secondary OCP. And a GES.
 

JoeStillman

Senior Member
Location
West Chester, PA
Feeding a transformer from a 208Y connected source does not mean you need a wye-connected primary. Nor does the fact that there are no neutral loads on the secondary mean that you need a delta connected secondary. The best transformer to use would be connected delta primary, wye secondary. You can ground the neutral point of the secondary and not run any neutral cables out to the load. It's better that way for lots of reasons.
 

darekelec

Senior Member
Location
nyc
Primary voltage is 120/208 Y 3ø.
150 kVA seems fine.
I will consider different transformers than Y/D. Good catch. 👍
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
With a 150kva you are looking at a 500 or 600 amp primary breaker.
 
I'm not so sure a150kva is necessary. From a load standpoint, I would expect the actual current to be about 95 amps, or only about 80kva. I would look at transformer efficiency at the current level, particularly since I assume this will be a fairly steady consistent load.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I'm not so sure a150kva is necessary. From a load standpoint, I would expect the actual current to be about 95 amps, or only about 80kva. I would look at transformer efficiency at the current level, particularly since I assume this will be a fairly steady consistent load.
It might come down to what transformer he can actually get in a reasonable time frame.
 