You are correct with the formula for the primary side full load current. But the nameplate shows the protective device rating.Can someone help me understand why this 20kva transformer is saying primary input 80A (see attached nameplate)
I feel it should be the following
20,000/240v=83.33/1.73=48.16
That does not make much difference, except it probably has a high inrush.I did notice it's an auto transformer.