Can someone help me understand why this 20kva transformer is saying primary input 80A (see attached nameplate)

I feel it should be the following
20,000/240v=83.33/1.73=48.16
 

Attachments

  • 02D1BE93-D051-4FE8-BFB6-8385F0F4D52D.jpeg
    02D1BE93-D051-4FE8-BFB6-8385F0F4D52D.jpeg
    546.4 KB · Views: 27

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
Can someone help me understand why this 20kva transformer is saying primary input 80A (see attached nameplate)

I feel it should be the following
20,000/240v=83.33/1.73=48.16
You are correct with the formula for the primary side full load current. But the nameplate shows the protective device rating.
The NEC suggests the primary side protection should be 125% of FLA. However, it allows up to 250%, when a 125% maximum secondary side protection is provided. These differences allow the protective device to handle the start up/in rush currents of the transformer.
 