Transformer for Microgrid Application - Confused

Status
Not open for further replies.

mrcole

New member
Location
Indianapolis, IN
I am currently working on a microgrid system that utilizes Ideal Power inverters (30C3):

http://www.idealpower.com/wp-content/uploads/2017/09/Stabiliti_30C3_DAT-00009_Rev-K_June17.pdf

These inverters are 3-wire 480V delta on the AC port. The inverters will connect to a 4-wire 208 wye generator bank. Per the recommendation of the inverter company, I was told a zigzag autotransformer could be used for this to derive a neutral for balance relative to ground. I've never used a zigzag (inter-connected star) transformer before and am unclear how this will work/is connected.

Another configuration that came up from speaking with transformer suppliers was a 480Y-to-208Y. This configuration was also not very clear to me given the 480V delta output of the inverters.

Has anyone encountered something like this before? Thanks.
 

pv_n00b

Senior Member
Location
CA, USA
Occupation
Professional Electrical Engineer
Let's see, you have a 480V 3ph 3W output from the inverter and you want to connect that to a 208V 3ph 4W system? According to the install manual, the inverter requires a 50A circuit breaker in the output circuit. If a 480V delta transformer is used then there will be no grounded neutral to trip the breaker in the event of a ground fault. So this is why they are saying a 480V delta will need a grounding transformer to make up a neutral. Or you can use a Wye/Wye transformer. You don't connect the neutral to the inverter.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Let's see, you have a 480V 3ph 3W output from the inverter and you want to connect that to a 208V 3ph 4W system? According to the install manual, the inverter requires a 50A circuit breaker in the output circuit. If a 480V delta transformer is used then there will be no grounded neutral to trip the breaker in the event of a ground fault. So this is why they are saying a 480V delta will need a grounding transformer to make up a neutral. Or you can use a Wye/Wye transformer. You don't connect the neutral to the inverter.

On the other hand in a truly ungrounded system a ground fault will not result in any fault current or hazardous voltage (except for the pump up from some arcing ground faults.)
I bet that the inverter output circuits would not be happy with the voltages of a corner grounded delta though, hence their concern about a ground fault.
 

Sahib

Senior Member
Location
India
On the other hand in a truly ungrounded system a ground fault will not result in any fault current or hazardous voltage (except for the pump up from some arcing ground faults.)
That is the main problem with ungrounded systems.:)
 

ggunn

PE (Electrical), NABCEP certified
Location
Austin, TX, USA
Occupation
Consulting Electrical Engineer - Photovoltaic Systems
Use a 480/277V wye to 208V delta step down transformer. Ground the center of the wye on the 480V side and that's your neutral.
 

Ingenieur

Senior Member
Location
Earth
what is the load on the 480 side?
another xfmr to tie into a utility? what config d:y, etc
or is it utilized at 480 on site?
multiple 208:480 sources bused together?
 