cgs5028
Member
- Location
- Rochester, NY, USA
Hello everyone,
I am looking for some opinions on how to go about sizing a transformer for a UPS. Any applicable code references are appreciated, though, other than transformer protection, I see no code dictating transformer sizing. Please correct if wrong.
We are replacing a UPS with a new unit.
The current installation is as follows:
30kVA transformer, 480 to 208Y/120, fed from (3) 40A fuses
80A fuses in 100A rated disconnect fed from transformer
UPS fed from disconnect.
The UPS will be replaced with a new 30kVA unit, unity PF, 30kW.
Data Plate Information:
Nominal Current: 89
Maximum Input Current: 102
Rec. OCPD: 150A
The UPS can be de-rated to a 20kVA unit with new
Data Plate Information:
Nominal Current: 59
Maximum Input Current: 68
Rec. OCPD: 90A
Since the method will be the same for both UPS ratings, lets just use the 20kVA for this question. Do I need to size the transformer so the rated secondary current is equal to or greater than the maximum input current, or the recommended over current protection device size, or for that matter, either?
For Max Input current: 68A*1.732*208V = 25kVA, meaning the existing transformer is large enough for this installation.
For Rec. OCPD: 90A*1.732*208V = 32kVA, meaning the existing transformer is not large enough for this installation.
From the code, I believe I can use the 30kVA transformer, primary protected only, at 125% ((30,000/(1.732*480))*1.25) = 45A, next fuse size up 50A. No secondary protection per 450.3(B). Then use the 90A fuses (manufacturer recommended) in the existing disconnect and size the secondary conductors accordingly.
The other opinion, is the transformer needs to be sized so the rated secondary current is equal to or greater than the Rec. OCPD. This would mean we need to install a 45kVA transformer since the calculation required a 32kVA, and the next size up in 45kVA. If we do not de-rate the unit (leave it at 30kVA), this opinion would mean we need to install a 75kVA transformer for a 30kVA UPS. That seems very oversized to me which kicked off this discussion and caused me to look into de-rating the UPS in an effort to use the existing transformer.
This transformer serves one dedicated load, the UPS. No possibility of expansion.
For those with more knowledge and experience than myself, I am curious what your thoughts are.
Thank you
I am looking for some opinions on how to go about sizing a transformer for a UPS. Any applicable code references are appreciated, though, other than transformer protection, I see no code dictating transformer sizing. Please correct if wrong.
We are replacing a UPS with a new unit.
The current installation is as follows:
30kVA transformer, 480 to 208Y/120, fed from (3) 40A fuses
80A fuses in 100A rated disconnect fed from transformer
UPS fed from disconnect.
The UPS will be replaced with a new 30kVA unit, unity PF, 30kW.
Data Plate Information:
Nominal Current: 89
Maximum Input Current: 102
Rec. OCPD: 150A
The UPS can be de-rated to a 20kVA unit with new
Data Plate Information:
Nominal Current: 59
Maximum Input Current: 68
Rec. OCPD: 90A
Since the method will be the same for both UPS ratings, lets just use the 20kVA for this question. Do I need to size the transformer so the rated secondary current is equal to or greater than the maximum input current, or the recommended over current protection device size, or for that matter, either?
For Max Input current: 68A*1.732*208V = 25kVA, meaning the existing transformer is large enough for this installation.
For Rec. OCPD: 90A*1.732*208V = 32kVA, meaning the existing transformer is not large enough for this installation.
From the code, I believe I can use the 30kVA transformer, primary protected only, at 125% ((30,000/(1.732*480))*1.25) = 45A, next fuse size up 50A. No secondary protection per 450.3(B). Then use the 90A fuses (manufacturer recommended) in the existing disconnect and size the secondary conductors accordingly.
The other opinion, is the transformer needs to be sized so the rated secondary current is equal to or greater than the Rec. OCPD. This would mean we need to install a 45kVA transformer since the calculation required a 32kVA, and the next size up in 45kVA. If we do not de-rate the unit (leave it at 30kVA), this opinion would mean we need to install a 75kVA transformer for a 30kVA UPS. That seems very oversized to me which kicked off this discussion and caused me to look into de-rating the UPS in an effort to use the existing transformer.
This transformer serves one dedicated load, the UPS. No possibility of expansion.
For those with more knowledge and experience than myself, I am curious what your thoughts are.
Thank you