Thank's in advance, this forum is always so much help!!
I'm installing a 30-kva 3 phase transformer. To feed a printing press. The press engineers want the xformer to change the feed from Delta to Wye. (Makes no sense to me 'cause there's no neutral to the press.And voltage they want is 230.) In taking advantage of existing circuits and parts, I'm setting it up this way; The input voltage is 235 volts. A 100 amp. OCPD feeding the primary, secondary out to a service rated disc. loaded with 100 amp fuses, to a 125 amp.rated sub. that has a 3 pole 50, and a 2 pole 30. To feed the press. With a total FLA at 125% of about 73 amps.
When I use the nameplate spec. of 240v. I calc that I need a primary OCPD size of 90 amp. (90.3) But if I use the actual input voltage I calc. to 92 amps. and can use the next highest OCPD at 100 amps.
Does anyone think the inspector will make me down size the primary OCPD to 90?
Or did I look at this incorrectly?
Rick
I'm installing a 30-kva 3 phase transformer. To feed a printing press. The press engineers want the xformer to change the feed from Delta to Wye. (Makes no sense to me 'cause there's no neutral to the press.And voltage they want is 230.) In taking advantage of existing circuits and parts, I'm setting it up this way; The input voltage is 235 volts. A 100 amp. OCPD feeding the primary, secondary out to a service rated disc. loaded with 100 amp fuses, to a 125 amp.rated sub. that has a 3 pole 50, and a 2 pole 30. To feed the press. With a total FLA at 125% of about 73 amps.
When I use the nameplate spec. of 240v. I calc that I need a primary OCPD size of 90 amp. (90.3) But if I use the actual input voltage I calc. to 92 amps. and can use the next highest OCPD at 100 amps.
Does anyone think the inspector will make me down size the primary OCPD to 90?
Or did I look at this incorrectly?
Rick