- Location
- New Jersey
- Occupation
- Journeyman Electrician
I'm working in a high rise building where all of the transformer GEC's are connected to a ground bus. This ground bus is connected to a common grounding electrode conductor that runs from the service room to top floor of the building. The building is structural steel construction and the connection of the transformer GEC is only to the common grounding electrode conductor. IMO since the building steel is available adjacent to the transformer the transformer GEC is required to connect to the nearest building steel as in 250.32(A)(7)(2). Does the installation of a common grounding electrode conductor negate the nearest connection requirement?
2008 NEC:
250.32(A)(7) Grounding Electrode. The grounding electrode shall be as near as practicable to and preferably in the same area as the grounding electrode conductor connection to the system. The grounding electrode shall be the nearest one of the following:
(1) Metal water pipe grounding electrode as specified in 250.52(A)(1)
(2) Structural metal grounding electrode as specified in 250.52(A)(2)