I received a building department comment that exactly reads:
It appears that an equipment grounding conductor from the transformer to panel ?K1? is sized per 250.122. The transformers are separately derived AC systems and the transformers have a grounding electrode system installed per NEC 250.66 & 250.30.
Situation:
I have a 112.5 kva transformer feeding a 400A MCB panel. I am using a parallel feeder of (4) #3/0 and (1) #3 EGC to feed my 208/3 panel from the transformer. I have a detail that shows a ground bus in the transformer, the ground bus has a GEC sized per 250.66 ( I used a 2/0) and coming out of the ground bus I have a EGC which is the #3 which goes to feed my panel. My detail also shows bonding jumper etc etc.
I think he wants me to run a 2/0 GEC to the panel if I am reading him correctly, am I missing something here? Is this correct??
It appears that an equipment grounding conductor from the transformer to panel ?K1? is sized per 250.122. The transformers are separately derived AC systems and the transformers have a grounding electrode system installed per NEC 250.66 & 250.30.
Situation:
I have a 112.5 kva transformer feeding a 400A MCB panel. I am using a parallel feeder of (4) #3/0 and (1) #3 EGC to feed my 208/3 panel from the transformer. I have a detail that shows a ground bus in the transformer, the ground bus has a GEC sized per 250.66 ( I used a 2/0) and coming out of the ground bus I have a EGC which is the #3 which goes to feed my panel. My detail also shows bonding jumper etc etc.