Goes from EMT to about 2' of flex (greenfield) that has an external bond (#6) on the outside. The ko is not cocentric so that's not an issue.
is it required to take the GEC (#4) and bring it to a bonding bushing and then to your "xo"? Or ground lug?
Thanks
Dex,
When installing an xfmr I bolt 2- 3 hole lugs to xo for the following connections:
1. EGC from supply feed
2. GEC to nearest GE
3. N to isolated neutral bar in load side disco(s)
4. BJ to xfmr case
5. System bonding jumper to ground bar in load side disco(s)
6. Internal BJ to load side disco(s) when using flex or liquidtight
An external BJ is limited to 6'.
It's not required to do it that way but it is required to be bonded. See 250.64(E)
Ya good way to do it for sure HotConductor.
Beaware the aluminum strap you see is most likely the transformer core bonding jumper and not the ox jumper.Dexie said:. The internal bond came that way with a strap internally. .
Beaware the aluminum strap you see is most likely the transformer core bonding jumper and not the ox jumper.
Thanks guys!
Well I have the GEC bonded directly to the XO. Are you saying I need to take another bond wire from the XO to the transformer chassis? Even if I have the GEC attached to the bonding bushing and then to the XO?
A "Bonding Jumper, System" to be exact.
Article 100
250.30(A)(1)