mikehughes8 said:I was under the impression that grounding electrodes were required at both locations whether there was bonding or not on a SDS.
(3) Grounding Electrode Conductor, Single Separately Derived System. A grounding electrode conductor for a single separately derived system shall be sized in accordance with 250.66 for the derived phase conductors and shall be used to connect the grounded conductor of the derived system to the grounding electrode as specified in 250.30(A)(7). This connection shall be made at the same point on the separately derived system where the system bonding jumper is installed.
This connection shall be made at the same point on the separately derived system where the system bonding jumper is installed.