I'm looking at an installation where two panelboards and dry type transformer are being replaced by two newer panels and a dry type and wanted to make sure that I thoroughly understood the attached transformer grounding detail. In this particular application a 480V panelboard is feeding a 45kVA transformer 480V-120/208V with a 50A breaker and the #8AWG secondary of the transformer feeds a 120/208V panel with #2 AWG and a 110A main breaker in the panel. Both panels and the transformer are currently mounted on a wall with a 1/4" x 2" ground bus located on the wall as well with a connection from the ground bus to the grounding electrode system (GES) using a 4/0 bare copper wire.
Currently the existing panels and transformers have a ground wire (I believe #6) running from the ground bar on the wall to the respective ground locations in the existing panels and transformer. I know that because the transformer represents a SDS a GEC is required to the transformer (assuming bonding jumper is at transformer) but is there a need to have the GEC's between the ground bar and the ground buses in the existing panels? When replacing this equipment with new equipment we are trying to decide weather or not we need to ground grounds from the ground bus in the panels to the ground bar on the wall. My understanding is that it is not required since we have the GEC to the transformer which is all that is required in this case. Is it a violation if we were to install these grounds between the panels and ground bus in addition to the GEC between the ground bus and transformer? Is this a good idea/practice or should we omit these when we install the new equipment?
I also noticed that the existing ground wires between the ground bus and panels/transformer, are run in rigid conduit (even though the distance is only a few feet on the wall). Isn't there a requirement in 250.64(E) to have these ground wires bonded to the conduit (with lay-in lug or similar) on both ends of the conduit? I noticed that the existing installation did not have this bond.
Looking at the attached detail I had a few questions I wanted to make sure I understood:
1) Is it necessary to bond the conduits in the panel and transformer to the equipment ground and ground bus as shown in the detail? Is there an NEC reference for this requirement?
2) Is 250.94 used to size the bonding jumper in the transformer as shown on the detail between the transformer neutral and ground? I do not see a table in this section so how is this size determined? Is 250.102 to be used?
3) In this case the GEC between the ground bar and transformer ground lug would be sized per 250.66. Since my feeder conductors to the panel are #2 AWG then it looks like I can use #8AWG as my GEC. Can this be run in conduit as discussed above or better off leaving this outside of conduit? Can I use any of the provisions of 250.66 A through C here?
4) I'm assuming that the Equpiment Ground Conductor (EGC) between the transformer and panel is sized per 250.122? In this case however there is no overcurrent device directly ahead of the panel so would I use the transformer primary breaker rating of the panel main breaker rating as the basis for choosing EGC from 250.122?
Thanks
Currently the existing panels and transformers have a ground wire (I believe #6) running from the ground bar on the wall to the respective ground locations in the existing panels and transformer. I know that because the transformer represents a SDS a GEC is required to the transformer (assuming bonding jumper is at transformer) but is there a need to have the GEC's between the ground bar and the ground buses in the existing panels? When replacing this equipment with new equipment we are trying to decide weather or not we need to ground grounds from the ground bus in the panels to the ground bar on the wall. My understanding is that it is not required since we have the GEC to the transformer which is all that is required in this case. Is it a violation if we were to install these grounds between the panels and ground bus in addition to the GEC between the ground bus and transformer? Is this a good idea/practice or should we omit these when we install the new equipment?
I also noticed that the existing ground wires between the ground bus and panels/transformer, are run in rigid conduit (even though the distance is only a few feet on the wall). Isn't there a requirement in 250.64(E) to have these ground wires bonded to the conduit (with lay-in lug or similar) on both ends of the conduit? I noticed that the existing installation did not have this bond.
Looking at the attached detail I had a few questions I wanted to make sure I understood:
1) Is it necessary to bond the conduits in the panel and transformer to the equipment ground and ground bus as shown in the detail? Is there an NEC reference for this requirement?
2) Is 250.94 used to size the bonding jumper in the transformer as shown on the detail between the transformer neutral and ground? I do not see a table in this section so how is this size determined? Is 250.102 to be used?
3) In this case the GEC between the ground bar and transformer ground lug would be sized per 250.66. Since my feeder conductors to the panel are #2 AWG then it looks like I can use #8AWG as my GEC. Can this be run in conduit as discussed above or better off leaving this outside of conduit? Can I use any of the provisions of 250.66 A through C here?
4) I'm assuming that the Equpiment Ground Conductor (EGC) between the transformer and panel is sized per 250.122? In this case however there is no overcurrent device directly ahead of the panel so would I use the transformer primary breaker rating of the panel main breaker rating as the basis for choosing EGC from 250.122?
Thanks