250.104 Bonding of Piping Systems and Exposed Structural
Steel.
(D) Separately Derived Systems. Metal water piping systems
and structural metal that is interconnected to form a
building frame shall be bonded to separately derived systems
in accordance with (D)(1) through (D)(3).
(1) MetalWater Piping System(s). The grounded conductor
of each separately derived system shall be bonded to the
nearest available point of the metal water piping system(s)
in the area served by each separately derived system. This
connection shall be made at the same point on the separately
derived system where the grounding electrode conductor
is connected. Each bonding jumper shall be sized in
accordance with Table 250.66 based on the largest ungrounded
conductor of the separately derived system.
Exception No. 1: A separate bonding jumper to the metal
water piping system shall not be required where the metal
water piping system is used as the grounding electrode for
the separately derived system and the water piping system
is in the area served.
Exception No. 2: A separate water piping bonding jumper
shall not be required where the metal frame of a building or
structure is used as the grounding electrode for a separately
derived system and is bonded to the metal water
piping in the area served by the separately derived system.
(2) Structural Metal. Where exposed structural metal that
is interconnected to form the building frame exists in the
area served by the separately derived system, it shall be
bonded to the grounded conductor of each separately derived
system. This connection shall be made at the same
point on the separately derived system where the grounding
electrode conductor is connected. Each bonding jumper
shall be sized in accordance with Table 250.66 based on
the largest ungrounded conductor of the separately derived
system.
Exception No. 1: A separate bonding jumper to the building
structural metal shall not be required where the metal
frame of a building or structure is used as the grounding
electrode for the separately derived system.
Exception No. 2: A separate bonding jumper to the building
structural metal shall not be required where the water
piping of a building or structure is used as the grounding
electrode for a separately derived system and is bonded to
the building structural metal in the area served by the separately
derived system.
(3) Common Grounding Electrode Conductor. Where a
common grounding electrode conductor is installed for
multiple separately derived systems as permitted by
250.30(A)(4), and exposed structural metal that is interconnected
to form the building frame or interior metal piping
exists in the area served by the separately derived system,
the metal piping and the structural metal member shall be
bonded to the common grounding electrode conductor.
Exception: A separate bonding jumper from each derived
system to metal water piping and to structural metal members
shall not be required where the metal water piping and
the structural metal members in the area served by the
separately derived system are bonded to the common
grounding electrode conductor