codequestion
Banned
- Location
- MD, USA
Attached is power riser and transformer grounding detail. The transformer grounding detail belongs to transformer T labeled #6 on power riser uses building steel and main service ground bar. NEC 2014 Article 250, Section 250.30(A)(4) says to have grounding electrode as metal water pipe or structural metal as grounding electrode. Exception No. 2 says grounding electrode used for the service or feeder equipment shall be permitted if originates in listed equipment. Attach picture transformer is 120 feet from switchboard. My question is transformer grounding detail is it per NEC 2014 Article 250.30(A)(4)?