Transformer grounding

Status
Not open for further replies.

reyamkram

Senior Member
Location
Hanover park, il
From what size kva Transformer you do not have to ground to a grounding electrode system? Can you just use the system grounding electrode conductor ? Where would I find it in the NEC article 250 what?

Thank you for any and all information
 
1KVa and less do not require connection to the GES.

250.30(A)
Exception No. 3: A grounding electrode conductor shall not be required for a system that supplies a Class 1, Class 2, or Class 3 circuit and is
derived from a transformer rated not more than 1000 volt-amperes, provided the grounded conductor is bonded to the transformer frame or
enclosure by a jumper sized in accordance with 250.30(A)(1), Exception No. 3, and the transformer frame or enclosure is grounded by one
of the means specified in 250.134.
 
1KVa and less do not require connection to the GES.

Now hold on, don't miss the important details in that exception...

250.30(A)
Exception No. 3: A grounding electrode conductor shall not be required for a system that supplies a Class 1, Class 2, or Class 3 circuit and is
derived from a transformer rated not more than 1000 volt-amperes, provided the grounded conductor is bonded to the transformer frame or
enclosure by a jumper sized in accordance with 250.30(A)(1), Exception No. 3, and the transformer frame or enclosure is grounded by one
of the means specified in 250.134.

Generally line power transformers need a connection to the GES.
 