Transformer Grounding

Status
Not open for further replies.

Gleybe

New User
Location
Rio de Janeiro, Brazil
Occupation
Electrical Engineer
Good Afternoon,

I am projecting a substation on the 3rd floor of a building with five delta-star 1250 kVA transformers and I need to ground its neutral to the metal structural frame of the building on the underground

Accordingly with table 250.66, the size of GEC have to be 3/0, is my understanding correct?

Thanks in advance for the help
 
Correct.
(Note the SBJ or SSBJ might be required to be larger)
 