Member
Grounding arrangement for a separately derived system in witch the grounding electrode conductor connection is made at the first disconnecting means or panel board.
After said that I am having a ruff time sizing the grounded conductor coming from the transformer XO to the nutral bus where everything is bonded together. I think you size the grounded conductor from the largest ungrounded service conductor and size from table 250.66 and if ungrounded service conductor is larger than 1100kcmil than multiply it by 12.5%. Is this correct and or is there more to the answer. based on the 05 code. thank you for the help
After said that I am having a ruff time sizing the grounded conductor coming from the transformer XO to the nutral bus where everything is bonded together. I think you size the grounded conductor from the largest ungrounded service conductor and size from table 250.66 and if ungrounded service conductor is larger than 1100kcmil than multiply it by 12.5%. Is this correct and or is there more to the answer. based on the 05 code. thank you for the help