In a delta-delta transformer for example - 75 kva - 240/480 pri-sec. In addition to equipment ground wire, which runs from the power panel, Is the equipment grounding to the nearest building steel require and what size?
A grounding electrode conductor is required from, the SDS to the structural metal and it would be sized per 250.66 based on the derived phase conductors.