At work contractor's installed qty. 3 PDU's at 250 kva each with no grounding electrode conductors per 250-30, which would require 2/0 copper to the building structural steel.
Sure, there are haphazard connections to the building steel from the primary side equipment ground, but that's not a GEC that's in the code, it's an error of omission. I wrote it up but the powers that be refuse to install the 2/0 copper GEC. Looking through the forums here I see it's also controversial on the boards, that omission of the GEC required by 250-30 (A) 3 is acceptable to some.
So that's what I mean, the grounding electrode conductor is required "shall connect, shall comply" in the manner specified. A wire sized by table connected to endpoints as specified.
I was told this is a gray area and pushing it makes me not a team playa. Employment issue.
The ionosphere is charged to hundreds of kV by radiation from space and the sun, mostly protons.
In dry air outside if you string a single conductor between trees on porcelain anchors, the wire will become charged to several kV from capacitive coupling to the ionosphere. Since dry air is a insulator, it will not pass enough power for a load. But if the wire charges then discharges through sensitive electronics, it may be enough to damage a tuner. Antennas are required to have earth grounding also.
If the same outside wire had a battery and lamp circuit but no earth ground, the entire circuit could operate at a static voltage well above ground. Moisture in the air would be enough to relieve this static charge.
A long time ago on the job, a nearby lightning strike hit the ground but there were several miles of overhead well pump control wires that I was called to work on to find out why they would not keep working. The overhead pump control wires picked up an induced voltage from the strike that came right out of the box I was working on. I was bent down over my tools at the time and the blast passed right over my back, turned everything a really pretty blue, and hit an antique 50 kW Terry steam turbo generator whose base I was using for a tool space. I was on the steam side when it hit. The plant manager had a chicken feed sized bag of bridge rectifiers that kept blowing out for that circuit.
There are other exercises. During fault clearing the equipment ground will have an elevated voltage due to the IR drop of current flow on the ground path. This is mitigated by complying and installing the GEC.
I write this because I am professionally curious about the "grey area". What are the reasons or code exceptions that allow not installing the GEC. I see this is controversial on these boards and at work.