Hey guys,
I'm running short circuit calculations for a feeder that has a step up 112.5 KVA transformer. The transformer has a temperature rise of 150 deg C.
The nameplate of the transformer states 6.3% for the transformer impedance, at 170 deg C. When I plug in the impedance value to determine the short circuit current on the transformer secondary, do I just use this value of 6.3%, or does one have to convert this value of 6.3% to something else, since this impedance is specifically at 170 deg C.
I'm running short circuit calculations for a feeder that has a step up 112.5 KVA transformer. The transformer has a temperature rise of 150 deg C.
The nameplate of the transformer states 6.3% for the transformer impedance, at 170 deg C. When I plug in the impedance value to determine the short circuit current on the transformer secondary, do I just use this value of 6.3%, or does one have to convert this value of 6.3% to something else, since this impedance is specifically at 170 deg C.