I have three transformers fed from the utility. The secondaries of these x-formers feed our plant with 3 phase 480 volts. It is currently wired with a wye primary and a delta secondary. Does the impedance of the three transformers change depending on how they are hooked up? wye-wye, wye-delta, or delta-delta? Hope this makes sense.
Thanks
 
robh said:
I have three transformers fed from the utility. The secondaries of these x-formers feed our plant with 3 phase 480 volts. It is currently wired with a wye primary and a delta secondary. Does the impedance of the three transformers change depending on how they are hooked up? wye-wye, wye-delta, or delta-delta? Hope this makes sense.
Thanks

No, the impedance is effectively per winding, regardless of the configuration.
 
The impedance of the system will change radically with changes in transformer connections. For example a grounded wye-grounded wye connection will have less L-G fault current because it "sees" the high side zero sequence impedance, whereas a similar sized delta-wye won't "see" the high side system impedance and will have a higher L-G fault current available.

Jim is correct that the transformer impedance won't change, but calculations relating to system impedance and available fault current will.

Jim T
 
Thanks for the responses. I would have guessed that the impedance of the x-formers would stay the same, but I couldn't find any information looking around the web to support my thoughts.
Thanks again,
Rob
 