Transformer Impedance

Status
Not open for further replies.

tryinghard

Senior Member
Location
California
What would be a common impedance percentage of a 480-120/240 112.5 KVA cu wound dry type transformer?

I want to calc the available fault current without calling the manufacture, at least get it close for design purposes if I can.
 

tryinghard

Senior Member
Location
California
I'm not purchasing just designing, our purchasing will have to call and it's not likely going to happen, I don't know who they'd use. Otherwise I agree I'd call.

I have a 83 KVA calculated load and there's no way I would buy a transformer without giving the site specific spes to the manufacture.
 
Last edited:

mivey

Senior Member
If you wind up being close on the AIC, I would bump it up. It kind of depends on what you are doing with the source impedance.

You could always call 2 or 3 manufacturers and use the worst case.
 
Transformer Question

Transformer Question

The System Discription:
Need to provide 480V/3ph with less than 160 milli-Ohms of resistance.

The installed system
Building service = 120/208V 3ph 4w --> 75KVA X-former (5.11% @ 170C) --> 480/277V 3ph 4w

I am measuring 11 m-ohms on primary side & 261 m-ohms on secondary.

What %impedance do I need to achieve < 160m-ohms?
Will a 112.5 KVA X-former achieve this?
Do I need a 150KVA ?
 