R retire09 Senior Member Aug 30, 2011 #1 Can a standard enclosed and vented transformer be installed in a Class I Div II location? 501.100(b) seams to say you can. Why would that be allowed?
Can a standard enclosed and vented transformer be installed in a Class I Div II location? 501.100(b) seams to say you can. Why would that be allowed?
rbalex Moderator Staff member Location Mission Viejo, CA Occupation Professional Electrical Engineer Aug 30, 2011 #2 They are allowed. For additonal enlightenment see 501.115(B)(2).