Transformer indoor

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
Indoor transformer 480V to 208/120V 75kva has system bonding jumper in the transformer. Has supply side bonding jumper to the secondary panel. No grounding electrode connection at the transformer

The transformer secondary panel has grounding electrode connection to building steel.

Does NEC 2014 require grounding electrode connection where system bonding jumper is located for the indoor transformer?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Yes
250.30(A)(5)
(5) Grounding Electrode Conductor, Single SeparatelyDerived System.
A grounding electrode conductor .................................................................................... This connection shall be made at the same
point on the separately derived system where the system bonding jumper is connected.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Yes
250.30(A)(5)
(5) Grounding Electrode Conductor, Single SeparatelyDerived System.
A grounding electrode conductor .................................................................................... This connection shall be made at the same
point on the separately derived system where the system bonding jumper is connected.
:)
 