Good morning all. Sort of a question.
I had a couple of transformers on a new installation. I have 100amp 277/480 feed to a panelboard that then serves these two 30KVA transformers. With no load on the system, if both 60 amp transformer breakers are switched on the feeder breaker trips due to inrush. Schneider suggested turning up inrush (I of i) dial based on their coordination study.
This got me thinking. A transformer is physically a dead short phase to phase.
Is it the magnetic field that opposes the short circuit current flow or the configuration of the phases?
Is the inrush caused by the build up of this magnetic field?
Hope these don't sound like stupid questions.
I had a couple of transformers on a new installation. I have 100amp 277/480 feed to a panelboard that then serves these two 30KVA transformers. With no load on the system, if both 60 amp transformer breakers are switched on the feeder breaker trips due to inrush. Schneider suggested turning up inrush (I of i) dial based on their coordination study.