Re: Transformer Inrush Problem
Yes, the inrushes would be higher as it is proportion as are the pri. and sec. voltages. So it appears high if the pri. sec. ratio is not taken into consideration. A 112.5kva, 480y-208y/120, 150degC transformer would have a pri FLA of 135a and sec. 312a. Anticipate the inrush to be about 1200a for the HV and 2800a on the LV.
If the cable feeding the transformer has been sized to carry the FLA of the transformer and the breaker feeding the transformer is sized accordingly you should never have a problem, either using a transformer to step up or step down with common 150degC rise transformers and you shouldn't with most others.
It's when the transformer is oversized for the load for which money is saved by running smaller cable and using a smaller breaker that starts to be an issue because the transformers inrush does not change.
My study was the result of a request made to me by a transformer marketing manager because no one had ever addressed it before. He had been confronted with nuisance tripping issues which was largely misunderstood. Combining my knowledge in industrial molded case circuit breakers and the anticipated inrushes of dry type distributions transformers of various designs (150, 115, 80degC, K-4, K13, etc). I put together a spread sheet using pri. only, and pri. if sec. protection is provided, with breaker magnetic trip values and calibration range.
Because my data is limited to that provided by one transformer design engineer I would welcome any credible inrush values from any other transformer manufacture to include in my data base.